Originally posted by MidwestCamper
View Post
I think keeping the bolted connections tight is key.
Crimped connections are what I use now.
I moved away from soldered connections to crimped as I went from being an electronics tech to an electrical tech and got involved with equipment wiring.
Joint Compounds. I've just used in outside environment connections.
I've used Kopr-Shield and "Penetrox E" for copper-to-copper or copper-to-silicon bronze.
I've used the Zinc based ones NoAlox, Penetrox A for aluminum-to-aluminum or aluminum-to-copper.
Thought back to the 2 month long downtime at one of our stations I had to work
The fire inside the switchgear was conductor phase to phase arcing and fire (probably from Corona degrading motor T leads insulation) inside metal clad switchgear that also shorted out the station's 12.47KV>4160V transformer windings.
The specialists from Dashiell just wanted denatured alcohol to clean the switchgear's bolted busbar, starters, arc chutes, cables & connections, etc.
No joint compound was used on any connections.
Couple of PDFs:
ELECTRICAL CONNECTIONS FOR POWER CIRCUITS https://www.usbr.gov/power/data/fist/fist3_3/vol3-3.pdf
https://www.bruker.com/fileadmin/use...ted_Joints.pdf
Thomas & Betts Kopr-Shield - https://www.mc-mc.com/ASSETS/DOCUMEN...0568638374.pdf
Penetrox E http://www.krimp-dsm.com/wp-content/...ccessories.pdf
Comment