    Hello electrically smart fellow campers. You know me, I still don't fully understand electricity. So I did a dumb thing tonight. I took my EMS out of line. It kept dropping service for a 2 minute reset showing a PE4, Low Voltage, error code. If I remember correctly it drops service at around 108V. I know 108V is really bad for air conditioners, but at this time we are not running A/C. Here is some more behavior information. When the power comes back on, and before the EMS enables, L1 and L2 are showing 120v and 122v. All good. But when the EMS activates the RV the L1 drops to 110 and L2 to 109. AMP draw is between 15 and 23. Well below the 30amp limit. Hmmm, watts going on here?

    Ok, I know that when you put 50amp units on 30amp posts over and over again the breaker gets worn and build up resistance. Ranger here assures me they have replaced the breaker recently. It is not warm to the touch at anytime. I am not thinking I have a weak breaker.

    Line drop from usage, that could be a possibility, we are strung out at the end of the line and I have no idea what else is connected. And it does tend to drop at times when other folks would be doing morning/evening chores/cooking etc.

    I am pretty careful about balancing our electrical usage on a 30amp post. Water heater and Refrigerator on propane settings. A/C set so that only one would come on, if it all. But we still get the PE4 low voltage disconnect.

    So I did the unthinkable tonight. I pulled the Progressive EMS out of the line.

    I know, I am asking for trouble. But I have had Progressive EMS get finicky and/or go south before. We will still mind our W's and V's and be real careful with the A/C units. Tomorrow I will dig out the old analog V meter and plug it in to watch and see what happens. At this point, I am kind of thinking the Progressive EMS is acting up. Definitely out of warranty.
    2017 Momentum 376, 2019 Ford F450
    2022 Triumph Scrambler Motorcycle
    E-bikes, Hobi Pedal Kayaks
    Kota the dog and KC the Kitty Cat

  • #2
    Your voltage reading before the amp draw hits it may be higher. Remember as load increases voltage may decrease if wiring is not large enough.

    As you stated, other items on the line increase usage or as you leg of feed (wiring not the breaker) warms up the voltage will drop (resistance increases as temperature of wiring increases).

    Think of the camp ground wiring as an extension cord. Lets daisy chain 4 - 100ft cords together and at each junction there are 3 outlets. One gets used to extend the length, the other 2 are open for load. If all 4 cords are the same size (14 gauge average size for home owner) with no load, the voltage at each of the plugs will be relatively the same. Lets now start adding load at each connection. the closest to source connection should always have the highest voltage, then second will be second highest, etc. if at each branch the load applied is 4 amps (don't want to trip the breaker) connection 1 sees 16 amps connection 2 sees 12 amps, connection 3 sees 8 amps and the end (connection 4) sees 4 amps. Cord 1 will get warm or hot, cord 2 less, cord 3 less, and cord 4 may not see any temperature change.

    Depending on how the sites are wired this could be the situation. If you are at connection 4 you see the most voltage swing. Likewise, to save money they probably downsized the wiring between each successive connection. So now you have a 12 gauge cord, a 14 gauge cord, and 2 16 gauge cords. The 12 is still overloaded due to length and total load., like wise with the 14, and the 3rd 16. The 4th 16 gauge is probably OK (except its under powered by the others).

    Hope this is not too long winded or complicated.
    Joseph
    Tow
    Vehicle: 2024 GMC K3500 Denali Ultimate Diesel
    Coach: 303RLS Delivered March 5, 2021
    South of Houston Texas

    Comment


    • #3
      Good plan to verify w/meter. Pls update when c/w
      Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

      2017 Ford F-350 DRW, '19 315RLTSPlus

      Comment


      • #4
        The voltage dropping that much when connected tells me there’s a problem in the park wiring. My guess would be a bad connection underground somewhere with high resistance. As you (and other on your line) increase their current draw the line is dropping voltage. This all assumes your EMS is reading properly obviously. Unfortunately not much you can do in this situation other than let the EMS do its job and disconnect you when the voltage drops.
        Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.​

        Neil Citro
        2018 Reflection 28BH Pepwave
        2019 F350 6.7L Long Bed Crew Cab

        Comment


        • #5
          Originally posted by Jlawles2 View Post
          Your voltage reading before the amp draw hits it may be higher. Remember as load increases voltage may decrease if wiring is not large enough.
          Hope this is not too long winded or complicated.
          Excellent description and I do understand what you said.


          Originally posted by ncitro View Post
          The voltage dropping that much when connected tells me there’s a problem in the park wiring.
          I mentioned the problem to the park ranger yesterday and he told me that they have had other complain about the problem. It's not something they are going to try and fix. I know that sounds shocking and irresponsible and normally would be except for the situation.

          We do volunteer campground hosting. Where we are at a state park that needed a host to fill in for a month while one of the more permanent hosts recovers from surgery. As a result we ended up in the "other" camphost spot, the one that is rarely used. We move on in a week. While the managers of the state parks do there best to keep the parks in excellent condition there are times when they have to do without to stay within their annual budget. Fixing this utility line for one host is not very cost efficient for them. He will put in for special funding, a "project". It will get sent up the line to HQ, HQ will prioritize projects and either fund it or not. But a single volunteer site is pretty low priority.

          In the mean time we get to enjoy a beautiful camp site. Now where did I put that darn voltmeter?

          Click image for larger version

Name:	175345014_10208489237744921_8628640873293193292_n.jpg
Views:	408
Size:	191.6 KB
ID:	51552

          2017 Momentum 376, 2019 Ford F450
          2022 Triumph Scrambler Motorcycle
          E-bikes, Hobi Pedal Kayaks
          Kota the dog and KC the Kitty Cat

          Comment


          • #6
            Ok more data. There is a huge fluctuation in voltage and there is a correlation to what we are drawing. Something somewhere is acting as a resistor. It's tempting to do a hot wire test to see where the problem is, but that would be rude, so I will just manage our usage until we leave.


            Pulling 6 amps
            Click image for larger version

Name:	20210422_100353.jpg
Views:	374
Size:	49.1 KB
ID:	51565


            Pulling 16 amps

            Click image for larger version

Name:	20210422_100401.jpg
Views:	361
Size:	52.6 KB
ID:	51566

            Pulling 3 amps

            Click image for larger version

Name:	20210422_101226.jpg
Views:	351
Size:	50.4 KB
ID:	51567
            2017 Momentum 376, 2019 Ford F450
            2022 Triumph Scrambler Motorcycle
            E-bikes, Hobi Pedal Kayaks
            Kota the dog and KC the Kitty Cat

            Comment


            • #7
              Looks like you are at the end of an undersized wire feed. A stepup transformer, autotransformer, would restore your voltage. You would then have a current limit. Can't get more power out than what is coming in.
              Ted
              2021 Reflection 310RLS
              2020 F350 PS,CC,LB,SRW

              Comment


              • #8
                Originally posted by d2reid View Post
                Ok more data. There is a huge fluctuation in voltage and there is a correlation to what we are drawing. Something somewhere is acting as a resistor. It's tempting to do a hot wire test to see where the problem is, but that would be rude, so I will just manage our usage until we leave.


                Pulling 6 amps
                Click image for larger version

Name:	20210422_100353.jpg
Views:	374
Size:	49.1 KB
ID:	51565


                Pulling 16 amps

                Click image for larger version

Name:	20210422_100401.jpg
Views:	361
Size:	52.6 KB
ID:	51566

                Pulling 3 amps

                Click image for larger version

Name:	20210422_101226.jpg
Views:	351
Size:	50.4 KB
ID:	51567
                Yep that sounds right. It’s a shame parks funding is where it is. Try to keep your current down, and keep your sensitive stuff off and should hopefully be okay

                Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.​

                Neil Citro
                2018 Reflection 28BH Pepwave
                2019 F350 6.7L Long Bed Crew Cab

                Comment


                • #9
                  Originally posted by TedS View Post
                  A stepup transformer, autotransformer, would restore your voltage. You would then have a current limit. Can't get more power out than what is coming in.
                  I wish it so, but it's not going to happen. So as usual, we roll with the flow... get it current..flow...



                  Originally posted by ncitro View Post
                  Try to keep your current down,
                  I had an instant reaction to these words. I was trying to imagine a current suppression system... all I got was some smoke above my head from trying to think to hard. We know how to manage our electrical usage. It took years to learn. Living in an RV is not the same as living in a house. No A/C usage, no convection oven usage, no air fryer, hair dryer only when everything else is turned off. For some reason DW considers a hair dryer an essential system.

                  What's fun is to put the bagels in the toaster. Instead of cherry red elements they are kind of brownish, takes longer to toast a bagel...

                  2017 Momentum 376, 2019 Ford F450
                  2022 Triumph Scrambler Motorcycle
                  E-bikes, Hobi Pedal Kayaks
                  Kota the dog and KC the Kitty Cat

                  Comment


                  • #10
                    You may try opening the power post and checking the plug and breaker lugs for proper torque and corrosion. Depending on when the park was built it may have AL wire which will corrode in the plugs and breaker causing a multitude of problems.
                    Joseph
                    Tow
                    Vehicle: 2024 GMC K3500 Denali Ultimate Diesel
                    Coach: 303RLS Delivered March 5, 2021
                    South of Houston Texas

                    Comment


                    • #11
                      Originally posted by Jlawles2 View Post
                      You may try opening the power post and checking the plug and breaker lugs for proper torque and corrosion. Depending on when the park was built it may have AL wire which will corrode in the plugs and breaker causing a multitude of problems.
                      I will give this a try today.
                      2017 Momentum 376, 2019 Ford F450
                      2022 Triumph Scrambler Motorcycle
                      E-bikes, Hobi Pedal Kayaks
                      Kota the dog and KC the Kitty Cat

                      Comment


                      • #12
                        Originally posted by d2reid View Post

                        I will give this a try today.
                        I would be surprised if they let you open the panel....I am also surprised they don't want/have the $$ to investigate. A significant voltage drop in wiring causes heat...heat can cause...fire..

                        At least you know it wasn't your EMS flaking out on you. It was doing it's job properly. Unlike the utility at the park.
                        2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
                        Electricians were created because engineers need heroes too....

                        Comment


                        • #13
                          Originally posted by Scott'n'Wendy View Post

                          I would be surprised if they let you open the panel....I am also surprised they don't want/have the $$ to investigate.
                          I wasn't going to ask permission. I am a huge believer in personal responsibility. So if I open the panel and screw up it's on me. I believe they don't have the money. A huge part of state parks budget comes from summer revenue. Close the state parks down for most of the summer their budget gets hit hard. State managers have got bigger problems on their plate than underfunded state parks. So 2021 is going to be a skinny budget year for the state park systems, as well as many other whose life's have been impacted by the shutdown.
                          .

                          2017 Momentum 376, 2019 Ford F450
                          2022 Triumph Scrambler Motorcycle
                          E-bikes, Hobi Pedal Kayaks
                          Kota the dog and KC the Kitty Cat

                          Comment


                          • #14
                            Originally posted by d2reid View Post

                            I wasn't going to ask permission. I am a huge believer in personal responsibility.
                            And I have no issue with that...except you said in the first post you don't completely understand electricity. Remember, even with the breaker off, there is still power in the box. Be careful.

                            2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
                            Electricians were created because engineers need heroes too....

                            Comment


                            • #15
                              Unrelated: That paint job is amazing!

                              Related: I had this issue a couple years ago in a heat wave. EMS shut down and I began moving items to gas and watching the voltage like the crew of Apollo 13. Was able to salvage the trip since AC was essential. I believe the EMS saved my AC.