    The Winegard Air 360+ and Gateway Router require a fused 12v/3A circuit. I'm considering using the bathroom circuit. Below is a diagram of what is on that circuit and the maximum circuit draw with everything on and going full tilt (including the vent being driven open in the bathroom).

    The red highlighted items are the powered devices--five overhead lights, two motion lights, and the fan in the bathroom.

    For the Winegard's on/off switch I'll tap the power coming in to the bedroom overhead light on/off switch (it's always "live"). Considering the maximum I read was ~5.3A on a 15A fused circuit, anyone see a problem with my plan? (The first BMV-712 screenshot shows the amperage draw with nothing on, or .7a. The second screenshot is with everything on circuit 4 running.)

    -Howard

    P.S. Ignore the "0%" on the BMV-712 readings shown below--I need to reset the state of charge (SOC).