After a few days this is where I am at with the transfer switch.
Renogy 2000 Watt inverter wired into the generator portion of the transfer switch.
I disconnected the live wire of converter from the breaker in the WFCO 8735, and ran a 12/2 wire from the transfer switch to the 8735, connected the ground and neutral to the panel, and bonded the live wires together.
Disconnected the 30 amp 10/2 wire shore power wires from the breaker panel and extended them to the transfer switch.
Wired the shore power 10/2 and the converter 12/2 into the shore power portion of the transfer switch.
Ran a new 10/2 wire from the panel portion of the transfer switch to the 30 amp breaker in the WFCO 8735.
What this accomplishes.
When I am on shore power the converter is powered and charges the batteries.
When I an on the inverter, the converter is disconnected by the transfer switch and does not charge the battery.
For those that are asking why do this, on the WFCO 8700 series, the converter is part of the panel and not a stand alone item.
A few things that I noted.
1) there is a 30 second delay in the transfer switch when turning the inverter on.
2) The connecters in the GoPower TS-30 are fickle, I had an issue with the inverter tripping a ground fault when it would transfer over. Turned out that I wasn't getting a good connection on one of the neutrals.
3) I have a 2022 23BHE, I assumed that I had a WFCO 8735, turns out I have the WFCO 8735-AD, which means that the converter auto detects if you are using Lithium, (I haven't upgraded to lithium yet, but I was trying to figure out how I was going to upgrade the converter. Don't have to now.
Renogy 2000 Watt inverter wired into the generator portion of the transfer switch.
I disconnected the live wire of converter from the breaker in the WFCO 8735, and ran a 12/2 wire from the transfer switch to the 8735, connected the ground and neutral to the panel, and bonded the live wires together.
Disconnected the 30 amp 10/2 wire shore power wires from the breaker panel and extended them to the transfer switch.
Wired the shore power 10/2 and the converter 12/2 into the shore power portion of the transfer switch.
Ran a new 10/2 wire from the panel portion of the transfer switch to the 30 amp breaker in the WFCO 8735.
What this accomplishes.
When I am on shore power the converter is powered and charges the batteries.
When I an on the inverter, the converter is disconnected by the transfer switch and does not charge the battery.
For those that are asking why do this, on the WFCO 8700 series, the converter is part of the panel and not a stand alone item.
A few things that I noted.
1) there is a 30 second delay in the transfer switch when turning the inverter on.
2) The connecters in the GoPower TS-30 are fickle, I had an issue with the inverter tripping a ground fault when it would transfer over. Turned out that I wasn't getting a good connection on one of the neutrals.
3) I have a 2022 23BHE, I assumed that I had a WFCO 8735, turns out I have the WFCO 8735-AD, which means that the converter auto detects if you are using Lithium, (I haven't upgraded to lithium yet, but I was trying to figure out how I was going to upgrade the converter. Don't have to now.