Disclaimer: In general, this forum is intended to be a place for Grand Design owners to gather and exchange ideas regarding their use of and experiences with Grand Design products. Any information contained in the forum should be independently verified by checking with Grand Design, one of its authorized dealers, or reviewing your owner’s manual.
If this is your first visit, be sure to
check out the FAQ by clicking the
link above. You will need to to register
before you can post: click the register link above to proceed. To start viewing messages,
select the forum that you want to visit from the selection below. Thanks for visiting and your interest in Grand Design!
I have a 310GK with factory Jaboni solar. On my unit the solar charges the batteries even when the disconnect is "off". When I pickup the rig from storage the batteries are fully charged.
Note: When the unit was new this was not the case. I found the batteries completely dead (like Frank W) a couple of times. The problem turned out to be a poor connection from the solar panels to the solar controller was causing intermittent failuers.
Mark
That's helpful information, Mark--thank you. I hope Willardsco sees this and checks to ensure his solar is working correctly.
Edit: I also see that was your first post. Awesome! Welcome to the technical forum and hope you'll continue to contribute.
Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.
Howard & Francine
2017 Ford F-350 DRW, '19 315RLTSPlus
I have a 310GK with factory Jaboni solar. On my unit the solar charges the batteries even when the disconnect is "off". When I pickup the rig from storage the batteries are fully charged.
Note: When the unit was new this was not the case. I found the batteries completely dead (like Frank W) a couple of times. The problem turned out to be a poor connection from the solar panels to the solar controller was causing intermittent failuers.
Mark
Not that Mark needs a backup but mine (I also have the 310 with solar option) was wired the same way with a wire right from the solar controller to the batteries - no disconnect (it was marked well). I plan to put a disconnect somewhere in the line from controller to batteries.