After seeing some issues with what I felt was premature battery drainage I looked at the factory solar controller and saw the fault light was on.
As I started measuring voltage I found that GD seemed to have wired the wires from the solar panels into the 25amp out and the battery routed into the solar input location.
After switching the wires over to the correct connection points the controller started charging the battery. The light was flashing green and i measured the voltage at the battery.
it was very disappointing to see it was misquoted from GD. I’m surprised that would t be caught in QC but I’ve felt that about a few things on this 2022 trailer.
The TLDR would be, if you see a fault light on your Furrion controller, verify your wiring.