Does Your EMS Shut Down When Running On a Generator?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • #16
    I just purchased a Honda Eu2200i and the Owners Manual says, "The generator (stator winding) is isolated from the frame and from the AC receptacle ground pin. Electrical devices that require a grounded receptacle pin connection will not function if the receptacle ground pin in not functional." Not being an electrician does that mean I need to use one of the grounding/bonding plugs that TucsonJim talked about? There is a Ground Terminal on the front of the unit, but not sure what I would need it for. Any and all thoughts would be appreciated.

    Comment


    • #17
      Originally posted by Dcn. Tom View Post
      I just purchased a Honda Eu2200i and the Owners Manual says, "The generator (stator winding) is isolated from the frame and from the AC receptacle ground pin. Electrical devices that require a grounded receptacle pin connection will not function if the receptacle ground pin in not functional." Not being an electrician does that mean I need to use one of the grounding/bonding plugs that TucsonJim talked about? There is a Ground Terminal on the front of the unit, but not sure what I would need it for. Any and all thoughts would be appreciated.
      Yes if you have a EMS protecting your rig you would need a bonding plug.
      Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

      Neil Citro
      2018 Reflection 28BH Pepwave
      2019 F350 6.7L Long Bed Crew Cab

      Comment


      • #18
        I have a 2021 Imagine 22MLE. Not sure if it has an EMS. Should I assume that the Owner's manual will tell me if I have one? Thanks for your feedback. Tom

        Comment


        • #19
          Originally posted by Dcn. Tom View Post
          I have a 2021 Imagine 22MLE. Not sure if it has an EMS. Should I assume that the Owner's manual will tell me if I have one? Thanks for your feedback. Tom
          An EMS is an option you add. It protects your rig from low voltage and other power issues in campgrounds. If you haven’t added one then you probably don’t have one (although you might want to consider it) and no neutral bonding plug will be needed.

          Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

          Neil Citro
          2018 Reflection 28BH Pepwave
          2019 F350 6.7L Long Bed Crew Cab

          Comment


          • #20
            ncitro

            While not needed to make an EMS "happy", why wouldn't a bonding plug still be a good idea (have the neutral bonded with a plug at the generator) so it becomes the "first disconnect means" as explained in the video linked in post 12?

            Let me hasten to add I'm asking because I am far from an expert on the topic--and if the EMS is looking for it isn't there a reason? Hopefully you or one of the other electrical types can expand on the rationale one way or the other.

            Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

            Howard & Francine
            2017 Ford F-350 DRW, '19 315RLTSPlus

            Comment


            • #21
              Originally posted by howson View Post
              ncitro

              While not needed to make an EMS "happy", why wouldn't a bonding plug still be a good idea (have the neutral bonded with a plug at the generator) so it becomes the "first disconnect means" as explained in the video linked in post 12?

              Let me hasten to add I'm asking because I am far from an expert on the topic--and if the EMS is looking for it isn't there a reason? Hopefully you or one of the other electrical types can expand on the rationale one way or the other.
              So I may have spoken out of turn, I was simply stating that with no EMS it would not be required. As far as a good idea or not, well I’ve always assumed there was a reason generator’s were designed with a floating neutral, and figured since they don’t even give you an option to bond it (without adding doing it yourself either via a rewire or bonding plug) that there would be no harm in using it that way. Hopefully someone with more knowledge than me will weigh in.

              Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

              Neil Citro
              2018 Reflection 28BH Pepwave
              2019 F350 6.7L Long Bed Crew Cab

              Comment


              • #22
                Originally posted by ncitro View Post

                So I may have spoken out of turn, I was simply stating that with no EMS it would not be required. As far as a good idea or not, well I’ve always assumed there was a reason generator’s were designed with a floating neutral, and figured since they don’t even give you an option to bond it (without adding doing it yourself either via a rewire or bonding plug) that there would be no harm in using it that way. Hopefully someone with more knowledge than me will weigh in.
                Yep, that would be my assumption, too. It's the why that has me curious. Why is it OK to not have the neutral and ground bonded from a generator (source of power) but the two wires are bonded from a campground's pedestal (source of power)?

                Mike Sokol's article RV Electricity – Generator neutral bonding basics talks a lot about the subject of the generator issue, but doesn't delve deeply into my question. Another google search ("RV Electricity unbonded danger") revealed hundreds of threads on the topic of bonded vs unbonded--I didn't realize it was such a debated subject.

                I do, however, find it interesting that onboard generators are bonded through the transfer switch when in operation and our Victron Multiplus' bond the neutral and ground when inverting...but it's OK to run an external generator without the bonding. ???

                My conclusion is it's one of those "scratch your head" topics that is just fun for electrical wizards to debate. Obviously people run their RVs all the time with an external generator without a bonding plug and their rig doesn't spontaneously vaporize...

                Howard
                Last edited by howson; 06-15-2021, 08:45 AM.
                Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                Howard & Francine
                2017 Ford F-350 DRW, '19 315RLTSPlus

                Comment


                • #23
                  If you do not use a n-g bond plug on a portable generator will the rv gfci receptacles work as the are supposed to work, i.e. interupt in the event of a ground fault? Without a n-g plug there will be no current path in the ground wire and the gfci will not detect the difference in current between the hot and neutral if there is a short to ground in the rv. Without current in the ground wire there would be no risk of shock with the floating neutral but the gfci may not work.
                  Ted
                  2021 Reflection 310RLS
                  2020 F350 PS,CC,LB,SRW

                  Comment


                  • #24
                    TedS -- even that GFCI issue was hotly debated in different threads I read on other forums!
                    Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                    Howard & Francine
                    2017 Ford F-350 DRW, '19 315RLTSPlus

                    Comment


                    • #25
                      Portable Generators with/without Bond to Neutral is a hard to wrap my head around, like why are companies allowed to build them that way.
                      The standards seemed to have different views about it.
                      ANSI/PGMA G300-2018 Safety and Performance of Portable Generators
                      ANSI/UL 2201 Mitigates Carbon Monoxide (CO) Poisoning for Portable Generators
                      NEC 250.34 Portable, Vehicle-Mounted, and Trailer-Mounted Generators
                      OSHA https://www.osha.gov/laws-regs/regul.../1926/1926.404

                      The most interesting and in depth site I found was Guy Holt's Local 481 GFCI Workshop - http://www.screenlightandgrip.com/ht..._Workshop.html
                      GFCI: Grounded Neutral Fault Detection Circuit.

                      Portable Generators - Half way down - (took me awhile to read that far)
                      Power Source Types: Floating Neutral generators, Bonded Neutral generators.

                      Systems Grounding and Equipment Grounding
                      Floating Neutrals vs. Bonded Neutrals, Floating Grounds vs Earth Grounds,

                      Portable Generators in Motion Picture Production - http://www.screenlightandgrip.com/ht...enerators.html

                      Older explanation of why <5kW portable generators don't have GFCI outlets
                      Portable Generators and OSHA Construction Regulations -
                      http://www.arrl.org/files/file/Techn...3-05%20(1).pdf

                      edit: Texas' electricity grid problems have me keenly interested in standby generators connections.
                      Last edited by gbkims; 11-02-2021, 10:57 PM.
                      Gene and Kim
                      2015 Grand Design Reflection 317RST
                      2017 RAM 3500 CC, LB, 4x2, 6.7L CTD

                      Comment


                      • #26
                        TucsonJimCate&Rob

                        Rob,
                        I'm told Jim's out of town...might you be able to offer any ideas on this??
                        Matt


                        Jim,
                        Couple questions hoping you can help with. Just bought a Champion 4500w dual fuel portable generator, model #200991.

                        Why would plugging in a home made bonding plug cause the generator to go into "Overload" and remove power output?
                        Do these require the brass grounding rod in the ground with wire to generator to operate?
                        (Thats what Champion told me on the phone)
                        I thought the "Bonding Plug" was used instead of the grounding rod & to allow power to pass through the EPO.

                        Manual states it has the "Neutral Floating", which is typical of these.
                        Started first try, warmed up for 5 minutes, but when I plug my "Bonding Plug" into the 20amp outlet the generator goes into "overload". Remove the bonding plug, reset the overload button and power output returns to normal, 120vac.

                        Will not work with my Hughes Autotransformer EPO connected. The EPO faults, as it should due to floating neutral, & doesn't let power apply.

                        When connected to rv directly from generator the power connects and will power the RV, EXCEPT the GFCI outlets will not work. Again, this is normal right?

                        I verified the bonding plug was wired correctly twice & had my neighbor verify too. Jumper from WHITE to GREEN (Neutral to Ground)
                        Could I have a bad plug? Its brand new.

                        Any ideas????

                        Appreciate any help,
                        Matt

                        btw...boy is the new 4500w model quiet and it ran my 13.5k A/C without an issue so really hoping this is an easy correction..
                        Last edited by S&M_G; 11-02-2021, 09:18 AM.
                        Sadie & Matt
                        (w/ 2d Mate Toby the traveling tabby)
                        2021 303 RLS
                        2020 Ram 2500 CC 4X4 w/6.7L Cummins
                        Andersen Ultimate Hitch

                        Comment


                        • #27
                          Originally posted by S&M_G View Post
                          TucsonJim
                          Jim,
                          Couple questions hoping you can help with. Just bought a Champion 4500w dual fuel portable generator, model #200991.

                          Why would plugging in a home made bonding plug cause the generator to go into "Overload" and remove power output?
                          Do these require the brass grounding rod in the ground with wire to generator to operate?
                          (Thats what Champion told me on the phone)
                          I thought the "Bonding Plug" was used instead of the grounding rod & to allow power to pass through the EPO.

                          Manual states it has the "Neutral Floating", which is typical of these.
                          Started first try, warmed up for 5 minutes, but when I plug my "Bonding Plug" into the 20amp outlet the generator goes into "overload". Remove the bonding plug, reset the overload button and power output returns to normal, 120vac.

                          Will not work with my Hughes Autotransformer EPO connected. The EPO faults, as it should due to floating neutral, & doesn't let power apply.

                          When connected to rv directly from generator the power connects and will power the RV, EXCEPT the GFCI outlets will not work. Again, this is normal right?

                          I verified the bonding plug was wired correctly twice & had my neighbor verify too. Jumper from WHITE to GREEN (Neutral to Ground)
                          Could I have a bad plug? Its brand new.

                          Any ideas????

                          Appreciate any help,
                          Matt

                          btw...boy is the new 4500w model quiet and it ran my 13.5k A/C without an issue so really hoping this is an easy correction.
                          Matt - Jim shared in a forum thread a few days ago that he will be /is now hunting more big game in northern AZ for about a couple weeks. He will be boon docking with no or very limited cell or internet service thus not active or on at all on the forum for that period.

                          Just wanted to share this if you were not aware in case Jim does not get back with you for sometume.

                          Dan
                          Dan & Carol
                          2014 303RLS Reflection #185 (10/2013 build)
                          2012 Silverado LTZ Crew Duramax 2500HD - 2700/16K Pullrite Superglide

                          Comment


                          • #28
                            Originally posted by Canyonlight View Post

                            Matt - Jim shared in a forum thread a few days ago that he will be /is now hunting more big game in northern AZ for about a couple weeks. He will be boon docking with no or very limited cell or internet service thus not active or on at all on the forum for that period.

                            Just wanted to share this if you were not aware in case Jim does not get back with you for sometume.

                            Dan
                            Thanks Dan!
                            Sadie & Matt
                            (w/ 2d Mate Toby the traveling tabby)
                            2021 303 RLS
                            2020 Ram 2500 CC 4X4 w/6.7L Cummins
                            Andersen Ultimate Hitch

                            Comment


                            • #29
                              Originally posted by S&M_G View Post

                              Thanks Dan!
                              That's strange behavior for sure, I've got the little brother to yours, the 3500 watt dual fuel and have no such issue. If it's tripping the overload I'd think the bonding plug was wired wrong and it was shorting the hot, but it sounds like you've checked that several times. I'd suggest checking the outlet on the generator to make sure it's not accidentally wired backwards, maybe they've got the polarity reversed somehow.

                              Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                              Neil Citro
                              2018 Reflection 28BH Pepwave
                              2019 F350 6.7L Long Bed Crew Cab

                              Comment


                              • #30
                                Originally posted by ncitro View Post

                                That's strange behavior for sure, I've got the little brother to yours, the 3500 watt dual fuel and have no such issue. If it's tripping the overload I'd think the bonding plug was wired wrong and it was shorting the hot, but it sounds like you've checked that several times. I'd suggest checking the outlet on the generator to make sure it's not accidentally wired backwards, maybe they've got the polarity reversed somehow.
                                Thanks Neil.
                                I'm on the phone with Champion again, but likely will have to do as you suggested. I just read a Mike Sokol article online & he said some of the Chinese ones "...don’t have a floating neutral, nor do they have a bonded neutral. Instead they make 60-volts AC on the hot wire, and 60-volts AC on the neutral wire. Sorry, but I don’t have a fix for that one.".
                                That should be easy to check with a multi-meter.
                                Champion Manual says "Floating Neutral" and Champion says generator is grounded to frame inside...interesting for sure. I'm going to try a second brand new bonding plug, as maybe I got a bad plug. No idea...
                                Sadie & Matt
                                (w/ 2d Mate Toby the traveling tabby)
                                2021 303 RLS
                                2020 Ram 2500 CC 4X4 w/6.7L Cummins
                                Andersen Ultimate Hitch

                                Comment