  • Automatic Transfer Switch testing

    I have a 15amp circuit feeding the RV via dogbone during the winter to keep the batteries charged when the battery heaters are going and the solar panel is covered in snow. This time I fired off my generator for a monthly run and didn’t unplug the 50amp connection first - normally only run the genset when there is no shore power. Popped a GFCI and CB in the house. I was under the impression that the Solitude has an Automatic Transfer Switch (sure looks like one behind the pass thru wall) and that the ATS would prevent back feed by cutting off power to the 50Amp connector in favor of the generator automatically. That didn’t seem to happen. Factory Onan and cabling (except for the LiFePO4s).

    From what I can read (nothing in the manual), there doesn’t appear to be any Warnings about disconnecting shore power before running the generator and the ATS should automatically adjust? Haven't had any spurious wiring or electrical problems at all. Just that this one surprised me - didn't expect any flow back into the house.
    Thanks,
    John

    2022 Solitude 310GK-R - Dual pane, factory solar, factory gen, 8K axles with discs, W/D, Heat Pump, Gen 2 Goosebox, Battleborn
    2020 Ram 3500 LB SRW 4WD Crew Laramie 6.7HO Aisin

  • #2
    May be mis-wired and the generator is not the default/preferred connection?
    Ted
    2021 Reflection 310RLS
    2020 F350 PS,CC,LB,SRW

    Comment


    • #3
      ajg617 Most of my ATS experience comes from motorhomes, but its a bad idea to switch them under load. The contacts in the relay will arc over as they switch from one source to another, and eventually will weld themselves into place and not switch anymore. That said, it should be pretty difficult for the ATS to cause what you saw, that would mean its somehow shorting the two inputs as well as the output. The first thing I would do if you have a meter and are comfortable working with electricity is unplug the rig, fire up the generator, and see if you have voltage at the power inlet to the RV. There should not be any, and if there is there is some kind of wiring issue. If there is not, then possibly a transient on the ground caused the GFCI and breaker in the house to trip. You would need a scope to see whats going on with that.
      Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

      Neil Citro
      2018 Reflection 28BH Pepwave
      2019 F350 6.7L Long Bed Crew Cab

      Comment


      • #4
        This article by Mike Sokol may help.
        https://www.rvtravel.com/rvelectrici...-switches-101/
        Ted
        2021 Reflection 310RLS
        2020 F350 PS,CC,LB,SRW

        Comment


        • #5
          Originally posted by ncitro View Post
          ajg617 Most of my ATS experience comes from motorhomes, but its a bad idea to switch them under load. The contacts in the relay will arc over as they switch from one source to another, and eventually will weld themselves into place and not switch anymore. That said, it should be pretty difficult for the ATS to cause what you saw, that would mean its somehow shorting the two inputs as well as the output. The first thing I would do if you have a meter and are comfortable working with electricity is unplug the rig, fire up the generator, and see if you have voltage at the power inlet to the RV. There should not be any, and if there is there is some kind of wiring issue. If there is not, then possibly a transient on the ground caused the GFCI and breaker in the house to trip. You would need a scope to see whats going on with that.
          The switching mode is break-before-make so that all sources are not connected to load when the switch occurs. Yes there is arcing as the source is disconnected from the load.
          Ted
          2021 Reflection 310RLS
          2020 F350 PS,CC,LB,SRW

          Comment


          • #6
            Originally posted by TedS View Post

            The switching mode is break-before-make so that all sources are not connected to load when the switch occurs. Yes there is arcing as the source is disconnected from the load.
            Yes thats right, thats why it should be impossible for the generator to backfeed the power inlet. I suspect a transient tripped the breaker, but best to check the inlet on the rig to make sure there is not something else going on.
            Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

            Neil Citro
            2018 Reflection 28BH Pepwave
            2019 F350 6.7L Long Bed Crew Cab

            Comment


            • #7
              Originally posted by ncitro View Post
              but its a bad idea to switch them under load. The contacts in the relay will arc over as they switch from one source to another, and eventually will weld themselves into place and not switch anymore.
              While what you say is true, it was just a 15a cct which will never draw much of an arc.

              2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
              2021 303RLS
              Electricians were created because engineers need heroes too...

              Comment


              • #8
                Originally posted by Scott'n'Wendy View Post
                While what you say is true, it was just a 15a cct which will never draw much of an arc.
                Yes the arc should not have been enough to cause an issue with the transfer switch, that was just advice to not let it switch under load.

                Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                Neil Citro
                2018 Reflection 28BH Pepwave
                2019 F350 6.7L Long Bed Crew Cab

                Comment


                • #9
                  If I understand correctly with Genset on and stabilized (I usually hear the click and 120V comes on), there should be nothing hot at the 50amp connector. If there is, I probably have an ATS that isn't doing its job correctly. I don't think I've ever kicked the genset on with shore power connected.
                  2022 Solitude 310GK-R - Dual pane, factory solar, factory gen, 8K axles with discs, W/D, Heat Pump, Gen 2 Goosebox, Battleborn
                  2020 Ram 3500 LB SRW 4WD Crew Laramie 6.7HO Aisin

                  Comment


                  • #10
                    Originally posted by ajg617 View Post
                    If I understand correctly with Genset on and stabilized (I usually hear the click and 120V comes on), there should be nothing hot at the 50amp connector. If there is, I probably have an ATS that isn't doing its job correctly. I don't think I've ever kicked the genset on with shore power connected.
                    I would do an audit of your wiring and thoroughly understand the operation of your ATS - read up on the manual. Then make sure you have correct wiring and the relay is not faulty.
                    2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
                    2021 303RLS
                    Electricians were created because engineers need heroes too...

                    Comment


                    • #11
                      Originally posted by ajg617 View Post
                      If I understand correctly with Genset on and stabilized (I usually hear the click and 120V comes on), there should be nothing hot at the 50amp connector. If there is, I probably have an ATS that isn't doing its job correctly. I don't think I've ever kicked the genset on with shore power connected.
                      That’s correct. If everything is working as it should you should not read any voltage between any of the pins at the power inlet on the side of the trailer when the generator is running.
                      Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                      Neil Citro
                      2018 Reflection 28BH Pepwave
                      2019 F350 6.7L Long Bed Crew Cab

                      Comment


                      • #12
                        Originally posted by Scott'n'Wendy View Post

                        I would do an audit of your wiring and thoroughly understand the operation of your ATS - read up on the manual. Then make sure you have correct wiring and the relay is not faulty.
                        Never received any manual - just went out an looked at it - WFCO WF-T57-R. Pretty clear label that says 20-60 seconds after starting generator, load will transfer from shore to genset. Measured voltage on the 50Amp plug pins - two read 5V and one read 7V. Suspect I have a leak somewhere.
                        2022 Solitude 310GK-R - Dual pane, factory solar, factory gen, 8K axles with discs, W/D, Heat Pump, Gen 2 Goosebox, Battleborn
                        2020 Ram 3500 LB SRW 4WD Crew Laramie 6.7HO Aisin

                        Comment


                        • #13
                          Originally posted by ajg617 View Post

                          - two read 5V and one read 7V. Suspect I have a leak somewhere.
                          Reference is really important. Need to make sure the neutral reference is solid...
                          This is why I was saying an audit (thorough check of the wiring) is needed.

                          2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
                          2021 303RLS
                          Electricians were created because engineers need heroes too...

                          Comment


                          • #14
                            Originally posted by ajg617 View Post
                            I have a 15amp circuit feeding the RV via dogbone during the winter to keep the batteries charged when the battery heaters are going and the solar panel is covered in snow. This time I fired off my generator for a monthly run and didn’t unplug the 50amp connection first - normally only run the genset when there is no shore power. Popped a GFCI and CB in the house. I was under the impression that the Solitude has an Automatic Transfer Switch (sure looks like one behind the pass thru wall) and that the ATS would prevent back feed by cutting off power to the 50Amp connector in favor of the generator automatically. That didn’t seem to happen. Factory Onan and cabling (except for the LiFePO4s).

                            From what I can read (nothing in the manual), there doesn’t appear to be any Warnings about disconnecting shore power before running the generator and the ATS should automatically adjust? Haven't had any spurious wiring or electrical problems at all. Just that this one surprised me - didn't expect any flow back into the house.
                            Thanks,
                            John

                            Your shore power wiring and generator wiring may be sharing a neutral. I would look over the wiring into the ATS to make sure the shore circuit and generator circuit are wired correctly (completely separate).

                            Allen

                            2021 Momentum 21G

                            Comment


                            • #15
                              Originally posted by acoleman43 View Post

                              Your shore power wiring and generator wiring may be sharing a neutral. I would look over the wiring into the ATS to make sure the shore circuit and generator circuit are wired correctly (completely separate).
                              I don't have an ATS, but would I be correct thinking it is a 3 pole contactor switching two hot legs and the neutral?
                              2018 Dodge 3500 6.7 Cummins w Aisin and 9 cup holders
                              2021 303RLS
                              Electricians were created because engineers need heroes too...