    The multiplus 2 is for a 50A two leg service (2 hot, neutral, ground). Can it be wired for just 30A one side (one hot, neutral, ground)? Having an unused open hot leg? if so it only has 3 wires in/ out for a 30A service, unless your upgrading to a 50A. You also don't show a connection from the batterys to the trailer buss bar powering the 12v side - should have a disconnect switch on that line too, 6 wag should work

    Now what is the rated discharge capacity of your batterys. Most I have seen are only 100A continuous (with a few seconds surge) the Multiplus in inverter mode pulls between 250 and 300 amps when fully used, more on surge. Depending on your batterys you may need a 3rd to not exceed the discharge rating.

    I have the Victron Multiplus 12/3000/120 and used 4/0 cabling, except for the batterys to my power in bar which I used 2/0.

    Folks double check my thought here.

    Keith
    Multiplus II can have a single phase or split phase input. By using the Multiplus II you allow more flexibility for future upgrades in my opinion. When I installed my system, the Multiplus II was only available for 12v systems. Because I went with a 24v system I went with the Multiplus 24/3000/70. but NOW they have the Multiplus II for a 24v system :(

    It looks like he is using Overkill BMS (missed this earlier....I do fully endorse Overkill BMS. They are excellent) on his batteries which limit continuous discharge to 120A. So max continuous discharge will be 240A (2 batteries), This may be his limiting factor in this system.

    howson I was thinking the same thing. A Cerbo would be nice....but would add an additional $600-$700 because you would want the GX Touch as well (I paid the extra and got the GX Touch 70...much better and worth the extra $$).
    Allen

    2021 Momentum 21G

    Comment


    • #32
      Thanks for great info!

      I was thinking about [maybe] to add CerboGX some time down the road, however did not put much emphasis on it. Maybe I don't understand the 'must have' of it.

      CurrentConnectthat I am ordering MultiPlus from; will upgrade to latest firmware and do programing according to my specs. I understand that there is a 'cool' factor of looking at color diagrams and flow of power in and out of batteries, solar etc. but once it is setup; what is there to 'monitor' every day?

      I am a techy, have built raspberry pi builds before, but I just don't get what is the need. Can someone set me straight how would this system would be beneficial to use on a daily basis?

      Is screen essential or CerboGX setup with a phone is essentially the same thing?

      Comment


      • #33
        2by4 It's key if you want monitoring when away from the rig. The Cerbo (or PI) allow connecting the device to the VRM portal so you can access the system and view status, change settings, or update firmware remotely. Also that's where you set your shore power for power assist. They do make an inverter control if you are not getting a Cerbo for just setting your shore power, but I always felt it was a waste to spend that money if you were going to be getting a Cerbo at some point anyway.

        https://battlebornbatteries.com/prod...caAvyAEALw_wcB



        If you're familiar with pi already, I think my pi with touchscreen rubbing Venus OS I had just over $100 into.

        Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

        Neil Citro
        2018 Reflection 28BH Pepwave
        2019 F350 6.7L Long Bed Crew Cab

        Comment


        • #34
          Originally posted by ncitro View Post
          2by4 It's key if you want monitoring when away from the rig. The Cerbo (or PI) allow connecting the device to the VRM portal so you can access the system and view status, change settings, or update firmware remotely. Also that's where you set your shore power for power assist.
          Found couple of pi3's in storage; one of them still with Emby install on SD card, also a usb wifi and a spare 32GB card. It appears I need an mk3-usb to connect pi to MPII. Thank you for the great tip! I'll check it out once I am more or less done on this main project.

          MPII is coming on Saturday; better start ordering wires.


          Originally posted by Yoda View Post
          Now what is the rated discharge capacity of your batterys. Most I have seen are only 100A continuous (with a few seconds surge) the Multiplus in inverter mode pulls between 250 and 300 amps when fully used, more on surge. Depending on your batterys you may need a 3rd to not exceed the discharge rating.
          Each BMS is 120A continuous discharge with 130A surge - at max it can provide 240A / 2880W, MPII is max 2400W; that should be enough as BMS would be at 82% max when MPII is maxed out.

          Comment


          • #35
            Another nice thing about the Cerbo GX and the Touch 50 is that it can be seen by anyone in the RV with out having to log into an App, easier for the wife to know what is going on or let me know what is going on if there is an issue. I do not have any wifi or such in our RV so that is not a help or even needed at this time. Also I do not even look at the Victron Connect app for any information, unless I am sitting outside the RV and am bored. You will like the ease of the Multiplus 2. I would double check the settings when you get it, just to make sure that it is exactly what you need for your system.

            Brian
            Brian & Michelle
            2018 Reflection 29RS
            2022 Chevy 3500HD

            Comment


            • #36
              Originally posted by 2by4 View Post
              Thanks for great info!

              I was thinking about [maybe] to add CerboGX some time down the road, however did not put much emphasis on it. Maybe I don't understand the 'must have' of it.

              CurrentConnectthat I am ordering MultiPlus from; will upgrade to latest firmware and do programing according to my specs. I understand that there is a 'cool' factor of looking at color diagrams and flow of power in and out of batteries, solar etc. but once it is setup; what is there to 'monitor' every day?

              I am a techy, have built raspberry pi builds before, but I just don't get what is the need. Can someone set me straight how would this system would be beneficial to use on a daily basis?

              Is screen essential or CerboGX setup with a phone is essentially the same thing?
              I wanted the Cerbo GX Touch so I can see a visual monitor while using the trailer, and so I have a place to tweak settings. I am also using the programmable relays of the Cerbo and wanted the VRM available to me. Future plans are to attach new tank sensors to the Cerbo (Via the GX Tank 140) for black, grey and fresh water, and for propane level sensors. That way I can have all my data in one location.

              I also have a Lynx Shunt that I'm able to see/use via the Cerbo. And, if time/money permits, I will convert the trailer to a split phase 50A and add an additional Multiplus for split phase operation. The Cerbo makes setup easier in my opinion.

              But, adding that to your system is an additional $600-$700. It's gotta be worth it to you to drop that kind of money.
              Allen

              2021 Momentum 21G

              Comment


              • #37
                Originally posted by acoleman43 View Post
                For DC wiring from Multiplus to distribution panel I would go with 4 awg.
                I had to spend some time digesting this info and I am a bit confused about this - Multiplus II does not have DC out to distribution panel, it is just AC 120V out to WFCO WF-8955PEC-GE
                Am I missing something in between or do I just run directly 4 AWG cable from batteries to DC bus on WFCO bus bar?


                Originally posted by acoleman43 View Post
                For AC I would look at something different than romex. I used romex and it wasn't the easiest to use in my installation - something like the Southwire flexible SOOW. I would go with 12/2 or 10/2. The larger the wire, the less voltage loss and heat....
                Thank you for recommendation; will get 10/2 SOOW wire at local hardware store by the foot.

                Comment


                • #38
                  2by4
                  The Multiplus is an inverter/charger. Or you could say it's an inverter/converter. Since the Multiplus is connected to the battery bank those 12vDC connections serve as both as an input from the batteries (for inverting) and also an output (to charge batteries and/or provide 12vDC to the camper).

                  Does that help?

                  Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                  Howard & Francine
                  2017 Ford F-350 DRW, '19 315RLTSPlus

                  Comment


                  • #39
                    Thank yo howson it definitely helps; to confirm on converter disconnect and which wires to run.


                    1. Disconnect the converter for 120V side:
                    A:black wire from "Converter" circuit breaker
                    B: neutral (white)
                    C: ground.
                    2. Disconnect converter from DC fuse side:
                    A: white
                    B: red
                    3. Run from Multiplus/batteries 4AWG wire:
                    A: red
                    B: black
                    4. Should the other 2 wires be disconnected from DC fuse side:
                    A: black
                    B: red

                    Click image for larger version  Name:	Converter disconnect.png Views:	0 Size:	755.5 KB ID:	105100

                    Comment


                    • #40
                      2by4

                      Disconnecting the OEM converter is easy. Turn off the breaker. Put a sticker over it (DO NOT TURN ON!) . Leave all the wires as they are so it will be easy to fire it back up upon the (slim!) chance the Multiplus fails or the trailer is sold (and you remove the Multiplus).

                      How the Multiplus is wired into the trailer depends on how you want it to power the system. Without an overall schematic showing how you intend to incorporate the Multiplus I'm hesitant to endorse the plan outlined in your previous post.

                      WondersAwait has an amazingly well done wiring diagram. See https://gdrvowners.com/forum/operati...lectrical-mods

                      If you want your mind blown, my rat's nest of a diagram is here: https://gdrvowners.com/forum/operati...lts-f-350-mods

                      Others have posted diagrams, too, but my mind is not firing on all cylinders rights now (tired).

                      Perhaps the diagrams below may help (or may just confuse you). The intent is to convey how my trailer was changed from the OEM configuration to what it is today (focused just on the +DC side).

                      The 120vAC side is an entirely different conversation.


                      Click image for larger version

Name:	12v DC Wiring Diagram v4 with OEM for comparison.jpg
Views:	255
Size:	182.1 KB
ID:	105106
                      Forum moderators are not GD employees--we are volunteers and owners presumably just like yourself. Unless specifically mentioned otherwise, we have nothing to gain should you choose to purchase a product or engage a service we discuss on this forum.

                      Howard & Francine
                      2017 Ford F-350 DRW, '19 315RLTSPlus

                      Comment


                      • #41
                        Originally posted by howson View Post

                        Disconnecting the OEM converter is easy. Turn off the breaker. Put a sticker over it (DO NOT TURN ON!) . Leave all the wires as they are so it will be easy to fire it back up upon the (slim!) chance the Multiplus fails or the trailer is sold (and you remove the Multiplus).

                        How the Multiplus is wired into the trailer depends on how you want it to power the system. Without an overall schematic showing how you intend to incorporate the Multiplus I'm hesitant to endorse the plan outlined in your previous post.
                        My plan was to disconnect WFCO converter and leave it in place; that's why I was planning to use 3A and 3B directly from batteries. I was just not sure about what are 4A and 4B (too much snow to get to RV now).


                        As for chassis power, I am not modifying anything there - from lithium positive 6AWG will go exactly to same spot on a bus bar where it was before.

                        Click image for larger version

Name:	original batteries.jpg
Views:	159
Size:	237.8 KB
ID:	105125

                        Updated diagram.

                        Click image for larger version

Name:	30A flowchart - 4.png
Views:	186
Size:	601.6 KB
ID:	105124

                        Comment


                        • #42
                          Originally posted by 2by4 View Post

                          I had to spend some time digesting this info and I am a bit confused about this - Multiplus II does not have DC out to distribution panel, it is just AC 120V out to WFCO WF-8955PEC-GE
                          Am I missing something in between or do I just run directly 4 AWG cable from batteries to DC bus on WFCO bus bar?




                          Thank you for recommendation; will get 10/2 SOOW wire at local hardware store by the foot.
                          Sorry about the misinformation. Howard is correct. Batteries go directly to distribution panel (through a fused connection). I think I got ahead of myself
                          Allen

                          2021 Momentum 21G

                          Comment


                          • #43
                            Originally posted by 2by4 View Post
                            Thank yo howson it definitely helps; to confirm on converter disconnect and which wires to run.


                            1. Disconnect the converter for 120V side:
                            A:black wire from "Converter" circuit breaker
                            B: neutral (white)
                            C: ground.
                            2. Disconnect converter from DC fuse side:
                            A: white
                            B: red
                            3. Run from Multiplus/batteries 4AWG wire:
                            A: red
                            B: black
                            4. Should the other 2 wires be disconnected from DC fuse side:
                            A: black
                            B: red

                            Click image for larger version Name:	Converter disconnect.png Views:	0 Size:	755.5 KB ID:	105100
                            4a and 4b should be +/- from batteries. No need to do anything with those.

                            For converter/charger, howson is correct, you can just flip the breaker. Knowing me (or my wife) I would flip is back on at some point not realizing what I did. I would disconnect either AC or DC side just to be safe. But that's up to you.

                            Allen

                            2021 Momentum 21G

                            Comment


                            • #44
                              Originally posted by 2by4 View Post

                              My plan was to disconnect WFCO converter and leave it in place; that's why I was planning to use 3A and 3B directly from batteries. I was just not sure about what are 4A and 4B (too much snow to get to RV now).


                              As for chassis power, I am not modifying anything there - from lithium positive 6AWG will go exactly to same spot on a bus bar where it was before.

                              Click image for larger version

Name:	original batteries.jpg
Views:	159
Size:	237.8 KB
ID:	105125

                              Updated diagram.

                              Click image for larger version

Name:	30A flowchart - 4.png
Views:	186
Size:	601.6 KB
ID:	105124


                              This is how I would do it.

                              Click image for larger version

Name:	M2.jpg
Views:	160
Size:	204.7 KB
ID:	105130
                              Allen

                              2021 Momentum 21G

                              Comment


                              • #45
                                Originally posted by 2by4 View Post
                                Thank yo howson it definitely helps; to confirm on converter disconnect and which wires to run.


                                1. Disconnect the converter for 120V side:
                                A:black wire from "Converter" circuit breaker
                                B: neutral (white)
                                C: ground.
                                2. Disconnect converter from DC fuse side:
                                A: white
                                B: red
                                3. Run from Multiplus/batteries 4AWG wire:
                                A: red
                                B: black
                                4. Should the other 2 wires be disconnected from DC fuse side:
                                A: black
                                B: red

                                Click image for larger version Name:	Converter disconnect.png Views:	0 Size:	755.5 KB ID:	105100
                                UGGGGGGGGG

                                Your converter is wired the same as mine was. . Take a look at this thread where I disconnected mine and trace the wires back. https://gdrvowners.com/forum/solar/5...-don-t-mess-up Sorry for the long read..
                                Do not touch 2a and 2b. You can leave them without any issue. There are two black (hot) wires connected to the breaker (wire nut). I left one attached (not the one from the converter) as I could not determine where it went. Then disconnected the ground (green) and negative return (white) and leave the rest in place just in case of failure. Be sure to wire nut and tape the wires you disconnected. Doing this would make it easy to reconnect if needed. No issues so far.
                                Hope this helps

                                Try and remember Murphy and the Kiss law.... Kip it simple.......Stu... I have learned this lesson many times here Mostly due to Howard, Jim, and Rob

                                Hoping to help
                                Keith
                                2018 Reflection 150 Series 220RK 5th whee, Star White 2022 F350 King Ranch CC Long bed (HAL) (CCC 4062lbs), B&W 25K OEM Companion,. SteadyFast system, Trailer reverse lights, rear receiver spare tire holder, storage tube, sumo springs, Victron MultiPlus 12/120/3000, Solar, Custom 6K axles upgrade, and other modifications.