Today I finished the Inverter installation. I re-routed the 6/3 line that went from the 50 amp inlet to the breaker panel. I was able to disconnect it from the panel and run it to the underbelly and forward to the inverter. Then I purchased 15 feet of 6/3 Romex from Lowes and install it in the underbelly from the inverter to the breaker panel.
The Multiplus II calls out two pair of 1/0 cable for less than 5 meters, and two pair of 2/0 for runs over 5 meters. I didn't have any 1/0 or 2/0, but had plenty of 4/0. So I ran a pair of 4/0 from the Lynx distributor to the Multiplus. 4/0, is not fun to work with - just sayin'. But I'll never have an issue with not enough ampacity in my wires..
I still need to run a chassis ground from the Multiplus and the Lynx components, but I hope to have everything up and running by Tuesday. I energized one battery tonight, and the Inverter started inverting. So at least that appears to be working.
I have ten 200 watt panels in the garage awaiting installation. I'll be down for six weeks starting on Thursday, so that will likely need to hold off until January unless my doc clears me sooner.
Jim
The Multiplus II calls out two pair of 1/0 cable for less than 5 meters, and two pair of 2/0 for runs over 5 meters. I didn't have any 1/0 or 2/0, but had plenty of 4/0. So I ran a pair of 4/0 from the Lynx distributor to the Multiplus. 4/0, is not fun to work with - just sayin'. But I'll never have an issue with not enough ampacity in my wires..
I still need to run a chassis ground from the Multiplus and the Lynx components, but I hope to have everything up and running by Tuesday. I energized one battery tonight, and the Inverter started inverting. So at least that appears to be working.
I have ten 200 watt panels in the garage awaiting installation. I'll be down for six weeks starting on Thursday, so that will likely need to hold off until January unless my doc clears me sooner.
Jim